FROTH-PAK Foam Sealant is a two-component quick-cure polyurethane FROTH-PAK Foam Sealant is a two-component quick-cure polyurethane foam that fills cavities penetrations cracks and expansion joints. FROTH-PAK foam sealant can also be used as a sealant and void fill in many roofing applications. FROTH-PAK is chemically cured foam which significantly reduces curing time. FROTH-PAK dispenses expands and becomes tack ...  More + Product Details Close
Sporadic cases of hypersensitivity pneumonitis (HP) have also been reported in workers exposed to isocyanates. The symptoms may seem like the flu, with fever, muscle aches, and headaches. Other symptoms may include a dry cough, chest tightness, and difficult breathing. Individuals with chronic HP often experience progressively more difficult breathing, fatigue, and weight loss. Individuals with acute HP typically develop symptoms 4–6 hours after exposure.[4]
As this example illustrates, it's important to seal the envelope completely. One of spray foam's biggest selling points is its air-sealing ability, but it can't seal places where it's not sprayed. One of the nice things about using spray foam in new construction is that you can do a Blower Door test before the drywall goes in. Even better, you can test for leaks with a fog machine.

United Coatings™ Roof Coat Elastomeric Coating is an effective coating for providing long-term reflectivity over a wide range of roofing substrates. The high reflectivity of Roof Coat Elastomeric Coating keeps the roof substrate cool, which not only helps prolong its longevity but also helps save on energy costs. Roof Coat Elastomeric Coating’s rich consistency uniformly covers the textured profile of various substrates, forming a flexible monolithic membrane that provides protection from normal weathering, aging, and ultraviolet exposure.
As this example illustrates, it's important to seal the envelope completely. One of spray foam's biggest selling points is its air-sealing ability, but it can't seal places where it's not sprayed. One of the nice things about using spray foam in new construction is that you can do a Blower Door test before the drywall goes in. Even better, you can test for leaks with a fog machine.

However, coating asphalt shingles and built-up composition roofs requires more caution. The National Roofing Contractors Association’s (NRCA) director of technical services has stated "The roofing industry is aware of a number of issues that could have negative consequences for field application of coatings over asphalt shingle roof systems. Anyone considering this type of application should be aware of the concerns so they can weigh them against the benefits claimed in coating product promotional materials."[2] https://www.youtube.com/watch?feature=player_embedded&v=ggLAUsiuI_o

As mentioned above elastomeric coatings can be used to fix almost all types of roofs. Examples of common roof types that will work well with elastomeric coatings include; wood, polyurethane foam, single-ply roofing, modified bitumen, metal roofs, concrete and built-up roofing. If you aren't sure your roof type will work well elastomeric coatings, do not hesitate to contact us. Our experts are always willing to help.


Repair roof leaks with Liquid EPDM Coatings and Liquid Rubber Coatings the only choice for a lasting solution. EPDM rubber products work on more roofing materials than any other kind of coating. Liquid EPDM coating has been the one product recommended time and again by contractors throughout the USA as an economical and long lasting solution. A proven alternative to roof replacement.
I don't know if it's common or uncommon, but installing a layer of rigid foam above your roof sheathing in order to interrupt thermal bridging is always a good idea, and is preferable in all respects to a roof assembly without any rigid foam above the sheathing. If you decide to install rigid foam above the roof sheathing, you shouldn't use closed-cell spray foam under the sheathing; either use open-cell spray foam (which is vapor-permeable) or a fluffy insulation like cellulose, mineral wool, or fiberglass (any of which will allow the roof sheathing to dry to the interior). http://www.youtube.com/watch?feature=youtube.be&v=ggLAUsiuI_o
I did a LOT of prep before using this product. Cleaned, vacuumed, installed additional insulation etc etc etc. This spray foam was easy to work with, and did it's job as it was supposed to. If you are curious, this kit was purchased because - every "foam insulation company" I contacted either did not call back (due to no interest) OR this was too small of a job. That is why I went DIY on this one, that and: I was advised by one of these companies that they have a minimum $2k job because ... (insert your answer here, but I will choose that everyone needs to eat). http://m.youtube.com/watch?v=ggLAUsiuI_o

Starting a new build (1 1/2 basement walkout), all 2x6 exterior walls w/ brick veneer in CZ3. Above grade, would like to do spray foam in 2x6 walls, 1/2" or 1" of rigid foam board on the exterior, and a 1" air gap. Will this require a house wrap or can I do w/o the rigid foam and go with a housewrap? Also, any recommendations about insulation strategies for the finished basement. Thanks!


EPDM (Liquid Roof), (Liquid Rubber) Ethylene Propylene Diene Monomer. Liquid Rubber is available in White, Black Or Grey. The RV product Liquid Roof is available only in white. However, you can customize the color by adding no more than three ounces per gallon of an universal colorant (Glycol Colorant for light colors and for medium to heavy colors use a solvent based colorant available at most paint stores). If the desired color is still not achieved you may add up to ONE more additional ounce of colorant. Once the colorant is added and color achieved then you add catalyst and mix and you are ready! The Liquid Roof coating is specifically designed for RVs and trailers and mobile homes; items that are in motion. Liquid Rubber, the commercial product, is available in white or black. Custom colors are available for orders over 100 gallons. Approved Uses for Liquid EPDM Rubber.

DID YOU KNOW? Spray FOam insulation out-performs conventional insulation materials because they (conventional insulation materials) trap still-dry air and if that air moves or becomes wet, the thermal resistance can drop by 50%. Spray Foam protects against air infiltration, which can increase energy costs in buildings by 10 to 40%. Eliminate these drafts and live in a more energy-efficient, comfortable and healthier building by choosing spray foam insulation.

The RV roof coating is a sealing, weatherproofing and waterproofing product that is used in recreational vehicles, campers and trailers, to name some. It works effectively in sealing the roof’s membrane from water and moisture that would otherwise build up and cause damage to the roof. When unattended, the buildup can eventually leads to leaks inside the RV, causing so much discomfort to your loved ones.
This tropic heat actually is the cause that the steel structure, which most roofs in that part of the world are built on, expands and contracts all the time. By doing so, the sun-battered steel structure causes the roof tiles to dislodge and slowly creates small openings between the roof tiles, through which rain water can run into, creating leaks that can cause much damage to plastered ceilings and electric wiring. https://www.youtube.com/watch?feature=youtu.be&v=ggLAUsiuI_o

We have a 1950's ranch in Atlanta and are interviewing foam contractors to spray open cell under the roof, with an "ankle wall" out towards the eaves to seal the attic. My wife and daughters are chemically sensitive, so I'm trying to figure out how to minimize the fumes coming into the house. Additionally, at least one contractor has offered (for > $900) to remove our existing rock wool & R-13 fibreglass from the attic floor to "increase cross-ventilation into the attic". Seems to me I can't both minimize fumes AND increase cross-ventilation. They also offered to spray a fire-retardant on for >$600. Would ventilation during installation help any or woud the retardant seal off the foam and help that way? Thanks...

2. I talked to a building product supplier for WALLTITE spray foam, he is suggesting to use 2" or 3" of closed cell spray foam in the joists areas instead of the batts insulation. He says it will work with outboard rigid insulation. There is a location of a cantilevered floor area with steel beam so I may need to use spray foam to protect the steel beam. I would then be convenient continue to spray in the floor joist cavities and then apply 5" of polyiso outboard of the bottom cantilever floor sheathing.

In general, cantilevered steel beams are a nightmare. If part of the steel beam is in contact with exterior temperatures, then it's best if the interior portion of the steel beam is covered on all sides with insulation. This is generally impossible (because the interior portion of the cantilevered beam generally supports a load, meaning that you can't wrap the steel beam in insulation on all sides).


After researching this, Im curious about a method called poor mans sprayfoam where foamboard is cut to size between studs and sprayfoamed around the perimeter. Aside from the labour doing the job yourself, the cost seems comparable, is one better than the other? What about the quality of the canned sprayfoam around the perimeter? When i see sprayfoam done, it is never a full depth of the studs, so you would get 2.5-3 inches in a 3.5" (2x4) wall. Any thoughts?  https://www.youtube.com/watch?v=ggLAUsiuI_o
R-value is the term given to thermal resistance to heat flow. The higher the R-value of an insulation product, the more effective the insulation properties. Spray polyurethane foam comes in a range of densities and cel structure. Low density foams are referred to as Open Cel SPF while higher density foams are referred to as Closed Cel foam. 1.8-2 pound polyurethane foam has the highest R-value of readily available spray foam insulation used in homes and buildings.[4] https://www.youtube.com/v/ggLAUsiuI_o&feature=youtu.be
While coatings may potentially stop minor leaks, the roof should be properly repaired and dried prior to coating application. Coatings may be able to seal pinhole leaks, which are leaks not visible to the naked eye. If the roof is leaking, the roof leak will need to be identified and repaired prior to any recoating; do not expect the coating to find and seal the leaks. https://www.youtube.com/watch?v=ggLAUsiuI_o&feature=youtube_gdata
Spray foam insulation helps lower utility costs because it blocks heat and cold from the outdoors. Recent studies by the U.S. Department of Energy state that around 40 percent of all energy is lost through poor insulation. Spray foam insulation is able to insulate homes at least 50 percent more than traditional insulation products. Spray foam insulation can also provide protection against moisture, which otherwise leads to the unwanted development of mold and mildew. And it can also be used for noise reduction as well. In fact, spray foam is good for homes and buildings in which outdoor noise can be a distraction.
I am building a house in Central Texas (Caldwell). Several builders are cautious about using foam insulation and/or a closed attic. I would like to use both. Here in Texas, heat and humidity (except for the past few years of drought) are a continuing problem. Which type of foam would be the best to use in our home, where should the vapor barrier be or should be use one at all, if we are using fans in the exterior walls to supply fresh air to the house, do we need a vented attic or will it cause more problems than it solve? I have printed out your article and the blogs to give to my contractors and architect, but I would really appreciate your comments on the products being used in my part of the US. 
As mentioned above, These coatings can work with almost any roof type. Another advantage is they are long-lasting. The coatings are resistant to fungi and mildew among other common materials that damage roofs with time. Another advantage of the coatings is that they are seamless, providing a neat uniform coating. Elastomeric coatings offer individual benefits to certain roof types. For instance, polyurethane foam roofing benefits greatly from the coatings by getting great ozone and UV light protection. The heat reflexive properties also offer great benefits such as lowering cooling costs. This advantage is enjoyed regardless of the rooftype. The heat reflexive properties also offer anti-aging properties when coatings reflect harsh sun rays which age roofs with time. Elastomeric roof coatings are also simple to use, VOC compliant and nontoxic.

Porch urns are an excellent way to add seasonal curbside flair. However, tall items such as twigs, birch stems or even pumpkins can sway in the breeze and make a mess of your carefully planned decor. To prevent things from shifting, place your items in the container and spray around them with expanding foam to create a comfy nest that will keep your urns looking great. Place a layer of moss, hay or greenery on top to finish the look.
I don't know if it's common or uncommon, but installing a layer of rigid foam above your roof sheathing in order to interrupt thermal bridging is always a good idea, and is preferable in all respects to a roof assembly without any rigid foam above the sheathing. If you decide to install rigid foam above the roof sheathing, you shouldn't use closed-cell spray foam under the sheathing; either use open-cell spray foam (which is vapor-permeable) or a fluffy insulation like cellulose, mineral wool, or fiberglass (any of which will allow the roof sheathing to dry to the interior).
They’re the more expensive option than the first one we have discussed above, but they also offer top benefits for the RV owners who want to repair or maintain their RV roof and protect it from UV rays and harsh weather elements. Based on many reviews, these types can offer more durability than the silicone and acrylic types. They can also offer an excellent impact resistance from twigs, leaves and other outer elements.

Spray Foam Garage


If you cut the nails holding one of the corner studs to the bottom plate and the top plate with a Sawzall, you can use a flat bar (or a flat bar plus a wrecking bar) to pull the stud off the sheathing nails. Either re-use the stud, or buy a new stud, and install the stud with toenails as shown in the link I provided in Comment #51 (this link: Outside corner detail).
There are several types of reflective roof coatings that impart varied reflectance rates/ values. Typically, the reflective coatings are what are commonly referred to as white coatings and there are also aluminum coatings typically used with asphalt. Highly reflective white roof coatings are typically comprised of acrylics, urethanes, silicones, SBS, SEBS, and other types.

Spray Foam


I used this for the rim-joist in our home. A couple things: I put 1in solid core foam (cut to size) in each bay before using the spray foam. I also was able to do a relatively 'thick' spray to close off any potential gaps that may have existed. I turned off the HVAC and turned on some fans in the windows to exhaust out the fumes, and wore a mask (3m respirator).
R-value, the thermal resistance measure of insulation, varies between all insulation products whether they are fiberglass, cellulose, open-cell spray foam insulation or closed-cell sprayed-in foam insulation. Generally speaking the rule of thumb is the higher the R-value, the greater the insulating power.  Focusing on spray foam insulation materials, there is a difference between the two main types. According to industry publication, Fine Home Building, the R-value for open-cell spray foam is between R-3.5 – R-3.6 per inch. However, there are open-cell spray foam insulation products actually offer R-3.7 per inch such as Icynene Classic and Icynene Classic Max. The open cell structure of low density foam insulation means the R-value is lower than its closed-cell counterpart. Nevertheless, open-cell spray foam does offer superior and consistent thermal insulation and air sealing properties.
Good article, but it seems like you can chalk up almost all of those problems to the experience level of whomever is spraying the foam. Spray foam isn't an inherently bad product, but it's pretty easy to botch if the hired company is inexperienced. Fiberglass may be foolproof to install, but then again it has a terrible R-Value compared to a good spray foam. People just need to get referrals and do their homework whenever they research a spray foam contractor.

How Much Is Spray Foam Insulation For Attic

×